Inspection, testing, tagging & repairing electrical equipment - OHS information sheet number 33

June 2009

The purpose of this information sheet is to ensure the inspection, testing and tagging of electrical equipment used at Monash University is conducted in accordance with the requirements of AS/NZS 3760:2003 In-service safety inspection and testing of electrical equipment and the Occupational Health and Safety Act (2004).

This information applies all electrical equipment used on the Australian campuses of Monash University and within Monash controlled entities. It covers University sanctioned activities by staff and students of Monash University, contractors, visitors, hire companies or any other person or agency associated with university activities.

Abbreviations

EPOD Non-fixed, electric portable outlet device (powerboard)
GPO General purpose outlet
RCD Residual current device

1. Who can test, tag and repair appliances?

1.1 All tagging and testing must be carried out by an approved person. An approved person may be a licensed electrician or a person who has completed the competency unit: Conduct in-service safety testing of electrical cord assemblies and cord connected equipment.

1.2 Only a qualified person may repair faulty electrical equipment. A qualified person shall be either:

1.3 Models that can be used to carry out testing and tagging of electrical equipment include:

Training a staff member Selection by the area manager of an appropriate staff member to be trained in the competency unit. The area may purchase or hire testing equipment
Facilities and services staff The area raises a BEIMS request to Facilities and Services to organise a contractor to test and tag the equipment
Contractor The area independently contracts a company to test and tag the equipment

2. Frequency of testing and tagging

The frequency of testing relates directly to the environment in which the equipment is used, the level of hazard and the degree of abuse to which the equipment is typically exposed. The frequency of testing is, in most cases, determined by the approved person.

A documented hazard assessment taking into consideration any relevant legislative requirements or guidelines must be conducted if deemed necessary to deviate from the standard testing frequency. A copy of this assessment should be kept with the records of testing.

For indicative purposes, electrical appliances shall be inspected and tested:

3. Priorities for testing

The following priorities are proposed for the implementation of testing of electrical equipment.

Note: New equipment does not need to be inspected or tested within 12 months of purchase, as the supplier is deemed responsible for the initial electrical safety of the new item. However, the responsible person shall ensure that the equipment is tested and tagged during the next testing schedule for their area.

3.1 Equipment in use

3.1.1 Laboratory/studio/workshop areas with use of electrical equipment by undergraduate and/or postgraduate students; electrical equipment in use in student residential accommodation; electrical equipment used in wet areas such as kitchens etc.

3.1.2 Laboratory/studio/workshop areas teaching facilities, lecture theatres, etc with use of electrical equipment.

3.1.3 Computer laboratories; multi-use areas such as libraries, sporting facilities, etc.

3.1.4 Office equipment.

3.2 Equipment not in use

3.2.1 Only equipment in use needs to be tested;

3.2.2 Equipment not in use and/or out of testing date should have an isolation tag to indicate tagging is required and must be tested prior to use.

4. Appliances brought in from home

Electrical appliances bought in by contractors or from home for use on a Monash site are subject to the same testing and tagging procedure for appliances owned or leased by the University. Appliances should be tested and tagged prior to their use on university premises.

While there is no requirement to test and tag personal laptops, staff and students are encouraged to have their laptops tested and tagged using an approved person or company.

In both situations above the testing and tagging is the responsibility and the expense of the owner.

5. Records of inspection and testing

Record to be kept by Academic/administrative unit/controlled entity
Records Records of inspection and testing of electrical equipment, including a:
  • Register of all electrical equipment; a record of formal inspection and tests
  • Repair register; and
  • Record of all faulty equipment
To be kept for: 5 Years

Appendix 1: Table 4 (AS3760:2003)

Type of environment and/or equipment Interval between inspection and tests
Class of equipment RCDs Cord sets and power boards
Class I
(Protectively earthed)
Class II
(Double Insulated)
Push button test by user
(Portable/Fixed)
Operating time and push button test
(Portable/Fixed)

1. Workshops, places of repair, manufacturing, assembly, maintenance or fabrication

6 months 12 months 3 months / NA 12 months / NA 12 months

2. Environment where the equipment or flexible supply cord is subject to flexing in normal use OR is open to abuse OR is in a hostile environment

12 months 12 months 3 / 6 months 12 / 12 months 12 months

3. Environment where the equipment or supply cord is NOT subject to flexing in normal use and is NOT open to abuse and is NOT in a hostile environment

5 years 5 years 3 / 6 months 2 / 2 years 5 years

4. Equipment used for commercial cleaning

6 months 12 months 3 months / NA 12 months / NA 12 months

5. Repaired, serviced and second hand equipment

After repair or service which could affect electrical safety, or on reintroduction to service

Notes:

  1. The actual sub environment in which the equipment is located determines the row for the environment to be used in Table 4, eg, A computer within a non-hostile environment in an office within a workshop or laboratory would attract a test/inspection action in accordance with Row 3
  2. Regulatory authorities, other standards, workplace safety requirements or manufacturer's instructions may specify intervals appropriate to particular industries or specific types of equipment
  3. Only equipment in use needs to be tested - equipment that is used irregularly can be tested immediately prior to use
  4. All workshop hand tools should be double insulated
  5. Unique experimental equipment: testing regime and frequency to be determined by work area for each case
  6. Fixed/ stationary equipment connected by a cable or flexible cord which is not flexed in normal use or exposed to damage nor in a hostile environment, is not normally considered to represent a hazard sufficient to warrant routine in-service electrical safety testing. However, where the flexible cable or cord is flexed on equipment which is moved for restocking, maintenance, cleaning, etc, in-service testing is considered to be required